News:

Calling all communications systems experts - please share your knowledge here!

Main Menu

INCOM Pass-Through Messaging via Modbus MINT

Started by Dave Loucks, April 05, 2012, 10:19:52 AM

Previous topic - Next topic

Dave Loucks

Changing Setpoints using INCOM Pass-Through on Modbus MINT
http://pps2.com/communications/files/INCOM/Modbus_INCOM_pass-through_V4.pdf

I've attached a link to a document that explains how to send INCOM commands through a Modbus MINT using something called INCOM pass-through.  The attached document includes example code written in VB2010, but the methodology would work for any programming language.  If you want a copy of the source code or the published (install files), you can download both from: http://pps2.com/files/mb/index1.php

The example I show is how to change a setpoint inside an automatic transfer switch controller (ATC-600 or ATC-800), but the method of writing an embedded INCOM message within the Modbus payload is the same.  Also, the method for changing setpoints within a device works with any INCOM device with a write-able setpoint buffer (e.g. OPTIM circuit breaker trip units, IQ/DT/MP/FP series protective relays, etc.)